Khacker
Mechanical
- Jul 19, 2010
- 2
I am currently trying to assist an owner with determing the reason for the continued failure of their domestic hot water heat exchangers. These are U-tube and bundle type HX's with the primary heating hot water circulating outside the tube bundle in the jacket. The tubes on the domestic water side of the HX's are erroding and pitting within 2" of the entry side of the tube sheet on the tubes. From the reading I have done it sounds like it could be an Erosion-Corrison failure. The domestic water is well water that is softened. We had circuit setters installed on the domestic side of each HX so we could measure the flow rate entering the HX's. They all seem to be within specifications both in flow (gpm) and velocity (approximately 6 fps). A friend of mine mentioned that if the cold water supply is connected to the entering side of the HX, it could be subjected to severe thermal shock. He also suggested that if indeed, high velocity within the tubes was the problem that more than likely you would have other failures throughout the tube bundles, particulary on the U-bends. Can anybody offer me any insight or point me in the right direction