Watertight louvre opening for Emergency Generator

Status
Not open for further replies.

aungkyawtun

Mechanical
Aug 20, 2008
32
Dear Gents,
IS there any standard for the sizing the exhaust louvre for the emergency generator's radiator.Now the caterpillar generator personel asking for the 150% of the radiator cross sectional area.
 
Replies continue below

Recommended for you

if you want Cat to stand behind their warranty on the generator, give them 150% or more. Or better yet, provide an exhaust fan which will provide posative ventilation.
 