HamidEle
Electrical
- Feb 20, 2007
- 309
We are in the process of choosing the control power supply for motors. Our client is a Eroupen company which dictates the applications. They object use of control transformer and want to use ac or dc ups for motor control power. They want to make sure the control power is always available to enable the motors reaccelrating if the power outages revovers within 0.5s. My concerns are, if there are so many motors recelerating simutaneously, large voltage dips may occur which may bring the system voltage further down and shutdown the whole plant. I don't have any operation experience with this applications. I appreciate it for any inputs.