Not sure if this is the right area to post this. If not please direct me to the proper area as I am new here.
To begin I will describe to you the area with the problem. The title indicates that I am having a weeping tile problem and am seeking a second opinion from what an engineer already informed me. I see some flaws in his logic. Mind you it would be a temporary fix but I can see down the road how his solution would cause more grievances and headaches. Also add additional funds to repair the problem. Here is his description and solution on fixing the problem. I will include my questions to him about my concerns which have yet to be answered.
I will also edit out pricing and names to safeguard his reputation and the fields pricing as this holds not bearings to my problem.
"
INTRODUCTION
We have had an opportunity to discern the problem of water penetration at the basement floor level at the exterior wall facing ****** Street. On June 12, 2003 the author visited the site and reviewed the condition of the water damage present at floor level along the exterior foundation wall. At the time of the site visit, moisture damage, dampness but no liquid water was visible. In addition, we reviewed the electronic photographs forwarded to us as well as a portion of the original foundation drawings. Apparently there was sufficient wetness that goods could not be stored in this area without incurring damage to the package goods. Although the LOCATION has been at this location for over 25 years, the moisture damage was noticed only in the last 12 months.
Engineering Company was requested to review the moisture damage and provide solutions to prevent future moisture ingress
Our comments and recommendations are presented below for your consideration.
OBSERVATIONS
According to the LOCATION, moisture had penetrated the north facing basement wall at floor level causing damage to the plaster at the base of the wall, debonding of several vinyl floor tiles and wetting the contents of adjacent stored products. The moisture damage was limited to about a 10 foot long stretch along the basement wall with adjacent areas along the wall showing no signs of moisture damage. The moisture damage extended up the wall plaster about 2 feet. The construction plans indicate that the exterior foundation wall consists of 12 reinforced concrete blocks with only the voids containing rebars being grouted. The other block voids were empty.
The basement floor level is approximately 8 feet below grade which is topped with a concrete sidewalk extending from the exterior wall to the curb along Soudan Street. A tree about 15 feet in height was located within 5 feet of the wall where the basement moisture damage was present.
At the time of the site visit no liquid water was observed. However, the bottom of the wall and adjacent floor tiles were damp. A view of the first floor joist space did not indicate any past or current signs of moisture penetration or wetness. A view of the sump in the basement floor did not indicate evidence of high water tables. The sump was almost dry and the Owner indicated that the sump was never used.
COMMENTS
The likely cause of water ingress is a temporary localized high water table created due to a blocked weeping system at that specific location. The proximity of the tree on the sidewalk could have caused the blockage of the weeping tile system as tree roots can easily penetrate the weeping tiles. The fact that the sump is relatively dry and that the moisture penetration appears to be localized to a relatively small portion of the exterior wall suggests that the weeping tile system effectively drains ground water in both directions from the blockage. One can envision rain water running down along the foundation wall until it reaches the weeping tile system and is effectively drained away thereby maintaining the water table below the top of basement slab and likely below the top of footing. However, at the blockage location, water running down the foundation wall can not easily or very slowly enters the weeping tiles and the water table temporarily rises up the foundation wall. In such a case provided there is sufficient water, the rain water can not only penetrate through the joint between the footing and the bottom of floor slab but also through the cracks and mortar joints in the foundation blocks. We noted the use of damproofing in the construction drawings. However, such damproofing is not effective at crack or joint locations. Eventually the water that has built up along the outside of the wall will drain down. However, until that happens water has an opportunity to enter and cause the observed damage.
RECOMMENDATIONS
1. The least expensive approach is to determine if a sewer snake used by plumbers can reach the supposedly plugged weeping tile location from the sump area. The author is not sure if this can be done as the type of connection from the weeping tile system to the sump is not known. The LOCATION may consider calling some one like A PLUMBER OR DRAIN SPECIALIST who for a minimal charge will come to the site and attempt to unplug the weeping tile system.
2. If the above suggestion is unsuccessful, we recommend that we drill 2 four inch diameter cores through the floor slab in the moisture damaged area. These cores would be next to one another one on top of the footing and one through the slab into the gravel subgrade. The cores would not be replaced for several weeks and the core holes observed for any collection of liquid water, especially after heavy rain falls and when interior wetness becomes visible. If liquid water does appear in the core holes to a height of the top of slab, a blocked weeping tile system will be confirmed as the likely cause of the moisture ingress. The solution in such a case would be to cut an interior drain form the wet area to the sump. This approach will be significantly less costly than digging from the outside.
"
Now option one is not feasible due to the fact that our weeping tile system has 12" clay tiles with 3/4" spacing. These gaps will prevent any snakes or optical cameras from being inserted. Entrance to the weeping tile is from the sump which T's off. From the T junction is approx. 15' feet to where we assume the blockage is.
Here are my questions I posted to the engineer regarding his method of repair.
"Hello *****,
I wish to thank you for pointing out a cost effective method that would fit our budget. But I have some concerns in the approach you wish to take. I realize I’m no engineer such as you. But I’d rather solve the problem once than find other problems associated with it down the road. Here are a few of my concerns.
This method is the most cost effective but is it the most effective method to remedy the problem. So we agree that this could spread over time. And when it does, from what I understand, is that additional drains would be incorporated further up the wall to alleviate the pooling of water on the other side.
With the depreciation of coverage the weeping tile has along the wall will this not cause further problems? And the drain that was originally installed becomes redundant with further collapse of the tiles? Even if the drain is not redundant will it also not cause problems with the cinder blocks on the other side of the wall as water and dirt may corrode the blocks and mortar?
Also with the drain being incorporated inside of the building will this also not cause a void when not only water but sand and dirt are also drained from the other side of the wall? Will this not cause a void and possibly collapse the sidewalk over time?
"
Any suggestions or thoughts from anyone would be appreciated. Just want to know if I'm over reacting and his method is a norm? Just that I never heard of an internal draining method before. Mind you his method is cost effective but I am not looking for cost alone. Don’t want to fork out additional funds later to find out I would have to end up digging outside anyhow.
Thank You.
John
To begin I will describe to you the area with the problem. The title indicates that I am having a weeping tile problem and am seeking a second opinion from what an engineer already informed me. I see some flaws in his logic. Mind you it would be a temporary fix but I can see down the road how his solution would cause more grievances and headaches. Also add additional funds to repair the problem. Here is his description and solution on fixing the problem. I will include my questions to him about my concerns which have yet to be answered.
I will also edit out pricing and names to safeguard his reputation and the fields pricing as this holds not bearings to my problem.
"
INTRODUCTION
We have had an opportunity to discern the problem of water penetration at the basement floor level at the exterior wall facing ****** Street. On June 12, 2003 the author visited the site and reviewed the condition of the water damage present at floor level along the exterior foundation wall. At the time of the site visit, moisture damage, dampness but no liquid water was visible. In addition, we reviewed the electronic photographs forwarded to us as well as a portion of the original foundation drawings. Apparently there was sufficient wetness that goods could not be stored in this area without incurring damage to the package goods. Although the LOCATION has been at this location for over 25 years, the moisture damage was noticed only in the last 12 months.
Engineering Company was requested to review the moisture damage and provide solutions to prevent future moisture ingress
Our comments and recommendations are presented below for your consideration.
OBSERVATIONS
According to the LOCATION, moisture had penetrated the north facing basement wall at floor level causing damage to the plaster at the base of the wall, debonding of several vinyl floor tiles and wetting the contents of adjacent stored products. The moisture damage was limited to about a 10 foot long stretch along the basement wall with adjacent areas along the wall showing no signs of moisture damage. The moisture damage extended up the wall plaster about 2 feet. The construction plans indicate that the exterior foundation wall consists of 12 reinforced concrete blocks with only the voids containing rebars being grouted. The other block voids were empty.
The basement floor level is approximately 8 feet below grade which is topped with a concrete sidewalk extending from the exterior wall to the curb along Soudan Street. A tree about 15 feet in height was located within 5 feet of the wall where the basement moisture damage was present.
At the time of the site visit no liquid water was observed. However, the bottom of the wall and adjacent floor tiles were damp. A view of the first floor joist space did not indicate any past or current signs of moisture penetration or wetness. A view of the sump in the basement floor did not indicate evidence of high water tables. The sump was almost dry and the Owner indicated that the sump was never used.
COMMENTS
The likely cause of water ingress is a temporary localized high water table created due to a blocked weeping system at that specific location. The proximity of the tree on the sidewalk could have caused the blockage of the weeping tile system as tree roots can easily penetrate the weeping tiles. The fact that the sump is relatively dry and that the moisture penetration appears to be localized to a relatively small portion of the exterior wall suggests that the weeping tile system effectively drains ground water in both directions from the blockage. One can envision rain water running down along the foundation wall until it reaches the weeping tile system and is effectively drained away thereby maintaining the water table below the top of basement slab and likely below the top of footing. However, at the blockage location, water running down the foundation wall can not easily or very slowly enters the weeping tiles and the water table temporarily rises up the foundation wall. In such a case provided there is sufficient water, the rain water can not only penetrate through the joint between the footing and the bottom of floor slab but also through the cracks and mortar joints in the foundation blocks. We noted the use of damproofing in the construction drawings. However, such damproofing is not effective at crack or joint locations. Eventually the water that has built up along the outside of the wall will drain down. However, until that happens water has an opportunity to enter and cause the observed damage.
RECOMMENDATIONS
1. The least expensive approach is to determine if a sewer snake used by plumbers can reach the supposedly plugged weeping tile location from the sump area. The author is not sure if this can be done as the type of connection from the weeping tile system to the sump is not known. The LOCATION may consider calling some one like A PLUMBER OR DRAIN SPECIALIST who for a minimal charge will come to the site and attempt to unplug the weeping tile system.
2. If the above suggestion is unsuccessful, we recommend that we drill 2 four inch diameter cores through the floor slab in the moisture damaged area. These cores would be next to one another one on top of the footing and one through the slab into the gravel subgrade. The cores would not be replaced for several weeks and the core holes observed for any collection of liquid water, especially after heavy rain falls and when interior wetness becomes visible. If liquid water does appear in the core holes to a height of the top of slab, a blocked weeping tile system will be confirmed as the likely cause of the moisture ingress. The solution in such a case would be to cut an interior drain form the wet area to the sump. This approach will be significantly less costly than digging from the outside.
"
Now option one is not feasible due to the fact that our weeping tile system has 12" clay tiles with 3/4" spacing. These gaps will prevent any snakes or optical cameras from being inserted. Entrance to the weeping tile is from the sump which T's off. From the T junction is approx. 15' feet to where we assume the blockage is.
Here are my questions I posted to the engineer regarding his method of repair.
"Hello *****,
I wish to thank you for pointing out a cost effective method that would fit our budget. But I have some concerns in the approach you wish to take. I realize I’m no engineer such as you. But I’d rather solve the problem once than find other problems associated with it down the road. Here are a few of my concerns.
This method is the most cost effective but is it the most effective method to remedy the problem. So we agree that this could spread over time. And when it does, from what I understand, is that additional drains would be incorporated further up the wall to alleviate the pooling of water on the other side.
With the depreciation of coverage the weeping tile has along the wall will this not cause further problems? And the drain that was originally installed becomes redundant with further collapse of the tiles? Even if the drain is not redundant will it also not cause problems with the cinder blocks on the other side of the wall as water and dirt may corrode the blocks and mortar?
Also with the drain being incorporated inside of the building will this also not cause a void when not only water but sand and dirt are also drained from the other side of the wall? Will this not cause a void and possibly collapse the sidewalk over time?
"
Any suggestions or thoughts from anyone would be appreciated. Just want to know if I'm over reacting and his method is a norm? Just that I never heard of an internal draining method before. Mind you his method is cost effective but I am not looking for cost alone. Don’t want to fork out additional funds later to find out I would have to end up digging outside anyhow.
Thank You.
John