Hi,
We have a pair of KEB VFD’s (319 kVA) installed in the field, driving a pair of turbo fans (250hp) within the same enclosure.
The power devices in order are MCCB – IR – VFD – Sine Filter – PMSM Motor. As mentioned, two sets are installed in the same enclosure, but they are fed from two different MCC cells. There is no other significant load, only a 500VA transformer for each.
The customer where it is installed reports to us that as soon as one of the MCCB’s is switched on, the line to ground voltage on the whole bus changes to:
L1-Ground ~130 volts
L2-Ground ~385 volts
L3-Ground ~365 volts
When both MCCB’s are OFF, voltage to ground is as you would expect: +/- 277VAC for each phase.
Note that the substation feeding the system has a delta-wye transformer (2.4kV to 480 VAC), with the wye grounded through HRG. They have also tried to ground our system to their building steel, with the same results.
Line to line voltages are stable at 479VAC. This situation is observed with the blowers NOT running.
I just can’t quite understand why the voltage to ground is affected that way, although the problem is tied to the VFD it seems. Any ideas?
Thanks.
We have a pair of KEB VFD’s (319 kVA) installed in the field, driving a pair of turbo fans (250hp) within the same enclosure.
The power devices in order are MCCB – IR – VFD – Sine Filter – PMSM Motor. As mentioned, two sets are installed in the same enclosure, but they are fed from two different MCC cells. There is no other significant load, only a 500VA transformer for each.
The customer where it is installed reports to us that as soon as one of the MCCB’s is switched on, the line to ground voltage on the whole bus changes to:
L1-Ground ~130 volts
L2-Ground ~385 volts
L3-Ground ~365 volts
When both MCCB’s are OFF, voltage to ground is as you would expect: +/- 277VAC for each phase.
Note that the substation feeding the system has a delta-wye transformer (2.4kV to 480 VAC), with the wye grounded through HRG. They have also tried to ground our system to their building steel, with the same results.
Line to line voltages are stable at 479VAC. This situation is observed with the blowers NOT running.
I just can’t quite understand why the voltage to ground is affected that way, although the problem is tied to the VFD it seems. Any ideas?
Thanks.