WBGT seems to be the definitive value used in heat stress situations. If conditions are dangerous to work in etc.
Various sources give ratings where people could work continuously as long as they are hydrated, and then as activity increases or the WBGT increases, hourly rest periods are prescibed.
Ultimately very minimal work is allowed per hour, and finally lethal levels are defined.
Anyways for indoor applications, with no sun beating down on you, my research finds a WBGT defined as:
WBGT = 0.7 x WB + 0.2 x GT +0.1 x DB
where WB is wet bulb, GT is globe temperature and DB is the dry bulb, all in degrees F.
My problem, I do not have a globe thermometer, I would have to fly one in and to use it in a continual data logging situation, it is going to be an expensive instrument, compared to something I could take spot readings with.
The globe thermometer is basically a 5 inch diameter hollow copper sphere, painted black, with a thermometer in the centre of the sphere. I guess the balck absorbs radiant heat, the sphere gives any air currrents a chance to cool it a bit. It would be nice to have a Globe Thermometer if you are truly into ASHRAE 55 studies etc, as those comfort zone charts never use the dry bulb temperature.
Anyways, I have a large concrete structure, people are working inside of it, there is not a lot of light, they do not have the sun beating on them.
I can easily come up with the same Heat Index the American weather channel or NOAA predicts, or the Humidex they use in Canada.
I have a lot of data logged 24/7 every minute, temperatures, dew points etc do not fluctuate that much. Not a lot of difference between the concrete temperature and the air temperature, very few spot cooling fans used. Its brutal in there, some floors averaged 90F with an 83 dew point.
I was wondering, how far off would I be, if I just used the dry bulb value in there as the globe temperature?
I think if anything, it would be making an error on the low side, I would get a low WBGT value?
The way we build has a far greater impact on our comfort, energy consumption and IAQ, than any HVAC system we install
Various sources give ratings where people could work continuously as long as they are hydrated, and then as activity increases or the WBGT increases, hourly rest periods are prescibed.
Ultimately very minimal work is allowed per hour, and finally lethal levels are defined.
Anyways for indoor applications, with no sun beating down on you, my research finds a WBGT defined as:
WBGT = 0.7 x WB + 0.2 x GT +0.1 x DB
where WB is wet bulb, GT is globe temperature and DB is the dry bulb, all in degrees F.
My problem, I do not have a globe thermometer, I would have to fly one in and to use it in a continual data logging situation, it is going to be an expensive instrument, compared to something I could take spot readings with.
The globe thermometer is basically a 5 inch diameter hollow copper sphere, painted black, with a thermometer in the centre of the sphere. I guess the balck absorbs radiant heat, the sphere gives any air currrents a chance to cool it a bit. It would be nice to have a Globe Thermometer if you are truly into ASHRAE 55 studies etc, as those comfort zone charts never use the dry bulb temperature.
Anyways, I have a large concrete structure, people are working inside of it, there is not a lot of light, they do not have the sun beating on them.
I can easily come up with the same Heat Index the American weather channel or NOAA predicts, or the Humidex they use in Canada.
I have a lot of data logged 24/7 every minute, temperatures, dew points etc do not fluctuate that much. Not a lot of difference between the concrete temperature and the air temperature, very few spot cooling fans used. Its brutal in there, some floors averaged 90F with an 83 dew point.
I was wondering, how far off would I be, if I just used the dry bulb value in there as the globe temperature?
I think if anything, it would be making an error on the low side, I would get a low WBGT value?