Vo_Dich
Mechanical
- Jul 24, 2018
- 2
I'm struggling to figure out if I can use a wet pipe sprinkler system for projects throughout California. Most of my projects are either single story commercial buildings or low-rise residential buildings with sloped roof, wood framed, and the insulation is at the ceiling. So any piping in the attic above the insulation has the potential to freeze or the attic space cannot be maintained above 40 deg F.
Per NFPA (2016) 8.16.4.1.1 Where any portion of a system is subject to freezing and the temperatures cannot be reliably maintained at or above 40 deg F, the system shall be installed as a dry pipe or preaction system. Which temperature do you gurus use to determine if you are above or below 40 deg F? It seems that most (if not all) cities in California I have looked at either in ASHRAE Handbooks, design winter dry bulb temperature either in EnergyPro or Trane Trace 700, the temperatures are all below 40 deg F. I have looked at weather.com, they list Average Low and Record Low for different cities. So which do you guys use? Does NFPA mention which to use?
NFPA mentions that you can put insulation covering over the sprinkler piping, but there are places where this can't be done, such as sprinkler heads in the attic, or sprinkler heads for the large overhang or patio area. Does NFPA allow pipe insulation? Mention of "insulation covering" and "tenting insulation" in NFPA leads me to thinking that this is not the same as pipe insulation.
Thanks in advance.
Per NFPA (2016) 8.16.4.1.1 Where any portion of a system is subject to freezing and the temperatures cannot be reliably maintained at or above 40 deg F, the system shall be installed as a dry pipe or preaction system. Which temperature do you gurus use to determine if you are above or below 40 deg F? It seems that most (if not all) cities in California I have looked at either in ASHRAE Handbooks, design winter dry bulb temperature either in EnergyPro or Trane Trace 700, the temperatures are all below 40 deg F. I have looked at weather.com, they list Average Low and Record Low for different cities. So which do you guys use? Does NFPA mention which to use?
NFPA mentions that you can put insulation covering over the sprinkler piping, but there are places where this can't be done, such as sprinkler heads in the attic, or sprinkler heads for the large overhang or patio area. Does NFPA allow pipe insulation? Mention of "insulation covering" and "tenting insulation" in NFPA leads me to thinking that this is not the same as pipe insulation.
Thanks in advance.