cda: to expand on Travis' post, NFPA 13 2010 22.4.4.5.1 states "For antifreeze systems greater than 40 gal in size, the friction loss shall aslo be calculated using the darcy-weisbach equation shown in 22.4.2.1.3 using a moody diagram, sigma factors that are representative of aged pipe, and adjusted k factors for fluid properties. The discharge from individual sprinklers shall be based on the adjusted k factors for fluid properties and shall be based on the following formula (look it up, don't feel like typing it out).
Basically, the equation is going to allow for the viscosity of the antifreeze based on your lowest expected temperature - if it gets real cold there, the liquid is going to be very thick, and not have the same hydraulic properties as water, so you're going to (possibly) see the pressure demand skyrocket.
Long story short, yeah they're going to have to re-calc, but make sure they calc right. The moody diagram is easy to flub if you're not looking real close at it.