edryder
Electrical
- Jun 25, 2004
- 4
If you seclect 75C conductors to feed a 400A panelboard two 3/0 (200A from table 310-16) per phase should work disreguarding all but the amp rating. My question is if 90C conductors were use instead would the amp rating be taken from the 90C column (225A) or the 75C column (200A). From what I understand from the NEC you would still use the amp rating from the 75C column if the equipment is rated for 75C conductor terminations.
Thank You,
Ed
Thank You,
Ed