What determines the maximum fill rate for hydrostatically testing large concrete tanks

Status
Not open for further replies.

HughRob

Mechanical
Aug 19, 2008
6
0
0
AU
Hi,
In Australia AS3735 states that the maximum fill rate for a hydro test is 2m per 24 hours, it is vague whether it has to be a uniform rate taking 24 hours (i.e. 2m/24 = 0.083m per hour) or could be achieved in a lesser period, let's say maybe 2m in 10 hours.

I appreciate that there should be a uniform rate that allows stresses and therefore strain to modify to minimize peak values, but it is unclear as to how the magical number of 2m per 24 hours has been defined and whether this is a maximum height per 24 hours or a maximum rate ?

Thanks in advance.
 
Replies continue below

Recommended for you


Copy and paste of the relevant statement at clause 7.3 TESTING OF LIQUID-RETAINING STRUCTURES;

(....structure shall be cleaned and initially filled with the specified liquid (usually water) at a uniform rate generally not greater than 2 m in 24 h...)

My guess is , max. uniform rate for 24 hours ( 2m/24 = 0.083m per hour)..