At the 8000HP+ range I would say the majority of motors are 13.8kV. Reducing current 1300A (at 4kV) down to 400A (at 13.8kV) makes cabling etc much easier.
Of course the greatest influence is the distribution system and what capacity already exists.
As to windings and voltages, look at the manufacturers experience lists and you will find the main suppliers will have years of experience at this voltage and this output. With regard to the winding types, the VPI system is used by all the major manufacturers and has well documented benefits and leads to a more reliable insulation system - I agree with Mendit that it requires process control, but this shouldnt be a problem if reputable a manufacturers is selected. There are plenty around: GE, ABB, WEG, Alstom would easily do this type of machine and larger.
In terms of reliability, we see many failed motors each year and the majoriry of failures are more due to abuse or poor maintenance than design or manufacturing error. I suggest that you always select a totally enclosed machine, TEWAC or TEEAC and fit appropriate condition monitoring and a regular maintenance regime.