I have a 60,000 sq ft warehouse that has an existing system that FM Global wants "reinforced" which can be interpreted as replaced.
See the layout below and it does appear to me we could meet FM's requirements on minimum spacing by installing a baffle on top of a W8 beam as shown in my sketch below:
One of the options given by the FM Field Agent was K16.8 upright sprinklers discharging 10 sprinklers @ 35 psi.
Luckily we have to deal with the beams, which have to be for wind bracing, on just the end of the building. I included a couple photo's to try to make things clear.
Look at figure 26 which appears to fit my layout. Anyone have experience with this?
See the layout below and it does appear to me we could meet FM's requirements on minimum spacing by installing a baffle on top of a W8 beam as shown in my sketch below:
One of the options given by the FM Field Agent was K16.8 upright sprinklers discharging 10 sprinklers @ 35 psi.
Luckily we have to deal with the beams, which have to be for wind bracing, on just the end of the building. I included a couple photo's to try to make things clear.
Look at figure 26 which appears to fit my layout. Anyone have experience with this?