What is 'Bubble Tight Shutoff' ? 3

Status
Not open for further replies.

Weegie

Petroleum
Feb 20, 2007
60
CA
Gents, I have researched this subject on these forums and found some good reference ANSI FCI 70-2 (old B16.104) and API 598 forum. I'm still confused though.
I have a vendor who quoted me 'bubble tight shutoff' for several full bore ball valves. No mention even of FCI 70-2 (Classes I thru VI for control valves - some ball valve companies do) or even API 598 on his literature. I looked through all the specs and can't find a definition of the Bubble Tight Shutoff term. (I've 'googled' it to death.)
Can anybody relate the term to a 'spec/standard/test' at all ?

Thanks.
 
Replies continue below

Recommended for you

Bubble tight means different things to different people, if your buying a valve from these guys specify the test you want to conform to there are several classifications that are used for valve tests as you have mentioned. Go back and have them confirm they conform to your requirements. That said my experience is bubble tight is synonomous with class V test level (but it wouldnt stand up in a court).
 
The term "bubble tight seal" is very old. My understanding is that it originated from a test where a valve was installed in an air system with an open end pointing up. Some soap was poured into the open end and air was applied to the other side. The valve passed if no bubbles formed in the soap. I'm not sure if this is true or not, but it was the only explanation I ever heard that was at least plausible.

David
 
Weegie,
I would interpret the requirement depending on the valve function, i.e.:

- as Class VI (to FCI-70-2 and/or IEC 60534-4 standards) for control valves;

- as compliant to Table 5 of API 598 standard for on-off valves.


But, as monaco8774 correctly says, this is just an interpretation (based on particular experiences...) and the best thing should be having the requirement explained by the Specifier himself.


About similar issues, see also thread408-172347 and thread408-150132 within this Forum (if you did not read them already).


Hope this helps, 'NGL
 
Thanks guys for the info and insight.
I checked the valve manufacturer's website and they directly state that many of their valve are available as per API 598, FCI 70-2.
I think I'm just dealing with a lazy salesman with limited technical knowledge of his product.
FYI, in my search of ball valve seat leakage info, I found another 'world' of specs out there developed by the "Manufacturers Standardisation Society".
They produce an MSS SP (Standard Practice) range for almost everything. (I came across MSS SP-61 Pressure Testing of Steel Valves.)

Thank again to all for their input.
 
Several MSS specifications may be applicable. A list follows:

SP-6-2001 Standard Finishes for Contact Faces of Pipe Flanges and Connecting-End Flanges of Valves and Fittings

SP-9-2001 Spot Facing for Bronze, Iron and Steel Flanges

SP-25-1998 Standard Marking System for Valves, Fittings, Flanges and Unions

SP-42-2004 Class 150 Corrosion Resistant Gate, Globe, Angle and Check Valves with Flanged and Butt Weld Ends

SP-43-1991 Wrought Stainless Steel Butt-Welding Fittings
(R 2001)

SP-44-1996 Steel Pipeline Flanges
(R 2001)

SP-45-2003 Bypass and Drain Connections

SP-51-2003 Class 150LW Corrosion Resistant Cast Flanges and Flanged Fittings

SP-53-1999 Quality Standard for Steel Castings and Forgings for Valves, Flanges and Fittings and Other Piping Components - Magnetic Particle Exam Method
(R 2002)

SP-54-1999 Quality Standard for Steel Castings for Valves, Flanges, and Fittings and Other Piping Components - Radiographic Examination Method
(R 2002)

SP-55-2001 Quality Standard for Steel Castings for Valves, Flanges, Fittings, and Other Piping Components - Visual Method for Evaluation of Surface Irregularities

SP-58-2002 Pipe Hangers and Supports - Materials, Design, and Manufacture

SP-60-2004 Connecting Flange Joint Between Tapping Sleeves and Tapping Valves

SP-61-2003 Pressure Testing of Steel Valves

SP-65-2004 High Pressure Chemical Industry Flanges and Threaded Stubs for Use with Lens Gaskets

SP-67-2002a Butterfly Valves

SP-68-1997 High Pressure Butterfly Valves with Offset Design
(R 2004)

SP-69-2003 ANSI/MSS Edition Pipe Hangers and Supports - Selection and Application

SP-70-1998 Cast Iron Gate Valves, Flanged and Threaded Ends

SP-71-1997 Gray Iron Swing Check Valves, Flanged and Threaded Ends

SP-72-1999 Ball Valves with Flanged or Butt-Welding Ends for General Service

SP-73-2003 Brazing Joints for Copper and Copper Alloy Pressure Fittings

SP-75-1998 Specification for High Test Wrought Butt Welding Fittings

SP-77-1995 Guidelines for Pipe Support Contractual Relationships
(R 2000)

SP-78-1998 Cast Iron Plug Valves, Flanged and Threaded Ends

SP-79-2004 Socket-Welding Reducer Inserts

SP-80-2003 Bronze Gate, Globe, Angle and Check Valves

SP-81-2001 Stainless Steel, Bonnetless, Flanged Knife Gate Valves

SP-82-1992 Valve Pressure Testing Methods

SP-83-2001 Class 3000 Steel Pipe Unions, Socket Welding and Threaded

SP-85-2002 Cast Iron Globe & Angle Valves, Flanged and Threaded Ends

SP-86-2002 Guidelines for Metric Data in Standards for Valves, Flanges, Fittings and Actuators

SP-88-1993 Diaphragm Valves
(R 2001)

SP-89-2003 Pipe Hangers and Supports - Fabrication and Installation Practices

SP-90-2000 Guidelines on Terminology for Pipe Hangers and Supports

SP-91-1992 Guidelines for Manual Operation of Valves
(R 1996)

SP-92-1999 MSS Valve User Guide

SP-93-1999 Quality Standard for Steel Castings and Forgings for Valves, Flanges, and Fittings and Other Piping Components - Liquid Penetrant Exam Method
(R 2004)

SP-94-1999 Quality Standard for Ferritic and Martensitic Steel Castings for Valves, Flanges, and Fittings and Other Piping Components - Ultrasonic Exam Method
(R 2004)

SP-95-2000 Swage (d) Nipples and Bull Plugs

SP-96-2001 Guidelines on Terminology for Valves and Fittings

SP-97-2001 Integrally Reinforced Forged Branch Outlet Fittings - Socket Welding, Threaded and Buttwelding Ends

SP-98-2001 Protective Coatings for the Interior of Valves, Hydrants, and Fittings

SP-99-1994 Instrument Valves
(R 2001)

SP-100-2002 Qualification Requirements for Elastomer Diaphragms for Nuclear Service Diaphragm Type Valves

SP-101-1989 (R 2001) Part-Turn Valve Actuator Attachment - Flange and Driving Component Dimensions and Performance Characteristics

SP-102-1989 (R 2001) Multi-Turn Valve Actuator Attachment - Flange and Driving Component Dimensions and Performance Characteristics

SP-103-1995 (R 2000) Wrought Copper and Copper Alloy Insert Fittings for Polybutylene Systems

SP-104-2003 Wrought Copper Solder Joint Pressure Fittings

SP-105-1996 (2001) Instrument Valves for Code Applications

SP-106-2003 Cast Copper Alloy Flanges and Flanged Fittings, Class 125, 150 and 300

SP-108-2002 Resilient-Seated Cast Iron-Eccentric Plug Valves

SP-109-1997 Welded Fabricated Copper Solder Joint Pressure Fittings

SP-110-1996 Ball Valves Threaded, Socket-Welding, Solder Joint, Grooved and Flared Ends

SP-111-2001 Gray-Iron and Ductile-Iron Tapping Sleeves

SP-112-1999 (R 2004) Quality Standard for Evaluation of Cast Surface Finishes - Visual and Tactile Method.

SP-113-2001 Connecting Joint between Tapping Machines and Tapping Valves

SP-114-2001 Corrosion Resistant Pipe Fittings Threaded and Socket Welding, Class 150 and 1000

SP-115-1999 Excess Flow Valves for Natural Gas Service

SP-116-2003 Service Line Valves and Fittings for Drinking Water Systems

SP-117-2002 Bellows Seals for Globe and Gate Valves

SP-118-2002 Compact Steel Globe & Check Valves - Flanged, Flangeless, Threaded & Welding Ends (Chemical & Petroleum Refinery Service)

SP-119-2003 Factory-Made Wrought Belled End Socket-Welding Fittings

SP-120-2002 Flexible Graphite Packing System for Rising Stem Steel Valves (Design Requirements)

SP-121-1997 (R 2002) Qualification Testing Methods for Stem Packing for Rising Stem Steel Valves

SP-122-1997 Plastic Industrial Ball Valves

SP-123-1998 Non-Ferrous Threaded and Solder-Joint Unions for Use With Copper Water Tube

SP-124-2001 Fabricated Tapping Sleeves

SP-125-2000 Gray Iron and Ductile Iron In-Line, Spring-Loaded, Center-Guided Check Valves

SP-126-2000 Steel In-Line Spring-Assisted Center Guided Check Valves

SP-127-2001 Bracing for Piping Systems Seismic-Wind-Dynamic Design, Selection, Application

SP-129-2003 Copper-Nickel Socket-Welding Fittings and Unions

SP-130-2003 Bellows Seals for Instrument Valves

SP-131-2004 Metallic Manually Operated Gas Distribution Valves

SP-132-2004 Compression Packing Systems for Instrument Valves


 
I have always crusaded against the term "Bubble tight shutoff".
A leakrate is completely meaningless unless there is a standard by which it is tested.

Many specifying engineers think that FCI 70.2 class VI is bubble tight, but there are specific numbers of bubbles allowed and there is a limited size range to which 70.2 Class VI applies. If an engineer specifies he wants class VI on a 10" valve...it's meaningless because 10" valves are not mentioned in that leak class.

Another confusion is that the standards specify the test conditions, but users expect the valves to meet the same leakage rates installed at completely different pressures and temperatures, and on different fluids. There is no predictable correlation.
 
I completely agree with JimCasey.


I only would like to add that "Leakage rate factors for Class VI" (see NOTE 2 to Table 3 of IEC 60534-4 and/or Table 2 of FCI-70-2) may be easily extrapolated also over the bigger size (DN 400 = ND 16") mentioned by the standards themselves, as it is clear that they are proportional to the square of the valve nominal diameter...


In general terms, extending the standards over their scopes and limitations is wrong and leads to contradictions or, at least, unpleasant messy situations... but unluckily it is a common practice among many Customers and Specifiers!! ;-P

Bye to All, 'NGL
 
Again gents, thanks to all for the insight and valuable help on this topic.

Best regards.

[two thumbs up]
 
I thought that Class IV for control valve still has a leakage rate (therefore, not bubble tight).

"Do not worry about your problems with mathematics, I assure you mine are far greater."
Albert Einstein
Have you read FAQ731-376 to make the best use of Eng-Tips Forums?
 
Ashereng,
yes, Class IV for has a large allowable leakage rate (1/1000 of the "rated valve capacity", whatever that is...).


Class VI instead is the tightest for control valves, "usually specified for critical applications where the control valve may be required to be closed, without a blocking valve, for long periods of time with high differential pressures..." (see FCI-70-2, para. 4.2.5).

Somebody finds appropriate to apply this Class to on-off valves too, especially when a measurement method more accurate than the visual one (e.g. with flow-meters) is used and gas test pressures are high, as the relevant allowable leak rates take in also test pressure in account (and not only valve size).



Hope this helps, 'NGL

 
anegri,

Ooops. Sorry. mis-read the VI vs IV.

Class VI still has a "leakage rate", based on port diameter, and a differential pressure.

In any case, all control valve leakage classes has a leakage rate - or, "NOT" bubble tight.

"Do not worry about your problems with mathematics, I assure you mine are far greater."
Albert Einstein
Have you read FAQ731-376 to make the best use of Eng-Tips Forums?
 
Yes,
Class VI allows from 1 (for ND 1" or less) to 45 (for ND 8") bubbles per minute, testing at 3.5 bar... but, for control valves, this may be still considered as a "TSO" (= tight shut off) or, better, a... "TESO" (= tight enough shut off) ;-)

Bye, 'NGL
 
OK. TESO it is.

"Do not worry about your problems with mathematics, I assure you mine are far greater."
Albert Einstein
Have you read FAQ731-376 to make the best use of Eng-Tips Forums?
 
*P.S.: "TESO" in Italian means strained, stretched, in tensione, worried... but why worrying about one bubble or two? ;-P

Have a nice week-end!! 'NGL
 
Good replies guys, and let me add a bit and summarize. First, I am glad you realize that "zero leakage" is not a reasonable expectation. The bubble test is size, pressure, media, and time dependent.

Most important, it is a bench test usually performed by the manufacturer, under clean conditions, at about 70deg.F. It is not valid after the valve is in service and contamination, different media,etc. will degrade the performance.

If one truly needs no leakage (and I am not defining that) then the system better accomodate leakage when it invariably will occur.



Paul
 
Many applications require positive shutoff. A double block and blead valve arrangement is often applied for positive shutoff. Zero leakage is specified in API STD 598 for soft seated valves. However, nasty hydrostatic testing fluid, welding slag and other such installation issues scratch surfaces thus eliminate "zero leakage" even if that was verified before the valve shipped.
 
Bubble-tight is a relevant term if applied to a certain set of conditions. It must be explained that way. For example, if you do an seat leakage test with air as permitted by API 598, ASME B16.34, MSS SP-110, and other standards, you can place a layer of water over the top of the seat being tested and look for free flowing bubbles. No bubbles during the test duration means it was "bubble-tight" and the valve passes the test. You will waste a lot of time testing tight sealing valves if you try to measure minute amounts of leakage with flow meters.

It is important to recognize that the factory test is strictly for quality. Are all the parts installed properly, are they manufactured correctly, etc. Never try to correlate the factory test with proof of performance. there are way to many variable and assumptions involved that the results are not vaild.

Bubble tight is a valid term provided it applies to specific, defined conditions.
 
Good post, bcd!

From a NDE/NDT standpoint, bubbles detection technique is one of the many recognized and standardized Leak Testing (LT) methods, having its own defined range of accuracy and application fields (i.e. for leaks location purposes only and a minimum detectable leakage in the range of 10[sup]-3[/sup] ÷ 10[sup]-4[/sup] Pa*m[sup]3[/sup]/s of gas flow, according to EN 1779 standard...).


See, for example:

- ASME Boiler & Pressure Vessel Code (2004 edition with 2006 addenda), Section V, Article 10, Appendix I and Appendix II;

- ASTM E515-05 "Standard Test Method for Leaks Using Bubble Emission Techniques" ;

- ;

- .


Hope this helps, 'NGL
 