All MV breaker have to have 'relays' to detect fault and open the breaker.
A breaker with proper relays, will open upon a fault but will not close automatically, untill commanded to do so, locally or remotely.
A recloser can be thought as a breaker with relays AND a timer/control circuit that will reclose the breaker one, two or three times (if keep tripping again) upon opening due to a fault. If the breaker trips after the third reclosing attempt, it will stay open. There are some variations as to how many reclosing attempts are made.
This is helpful to restore the service automatically in case of a transient or mometary self clearing faults, for example one caused by two overhead lines coming in contact in a windy conditons, but clearing itself or a falling of tree limb etc.
If you wanted to know how to spec a recloser that is a differnt story. Post the question accordingly if so.