I am trying to design a air conditioning system for a chicken farm about 25000 chickens. But I am in trouble with heat gain for chickens and the ammonium effect about the dirt of chickens. Can anyone help me with this huge farm design. Thanks.
 
Replies continue below

Recommended for you



Sensible and Latent Heat Production for Animals:

Broilers:

0.22, 84.2, .0009, .9208, 4.1
1.5, 60.8, 0.0108, 11.3, 14.3
1.5, 77.0, 0.0046, 4.8, 16.7
1.5,86.0 0.0154, 16.1, 14.3
2.4, 60.8, 0.0109, 11.4,,13.5
2.4, 66.2, 0.0044, 4.6, 26.3
2.4, 86.0, 0.0243, 25.3, 15.0
3.5, 66.2, 0.0071, 7.4, 31.1
4.4, 66.2, 0.0062, 6.4, 32.8


The values are (From Left to Right):
1. Animal Wight (lbs)
2. Temperature (F)
3. Water Production (lbs of H20 per animal-hour)
4. Sensible Heat BTU/animal-hour
5. Latent Heat BTU/aniaml/hr

This information is from the Midwest Plan Service, Structures and Environment Handbook, 1993, 11th Ed.
Table 633-1 page 633.3
ISBN 0-89373-057-2
It is a pretty handy book, especially if you are designing a farm. Most of the values in the tables are for smaller farms.

I don't really know where to get it. It was a textbook for a class when I was an Ag. Engineering Student at Cal Poly SLO.

I hope this is helpful.

Jeff Johnson
Schreiber Engineering
jjohnson@trueton.com
 
Thanks ClydeMule for your answer. I am new to hvac applications and I am very happy with your answer. But when I found a 2000000 Btu/h heat gain for my broiler chicken farm I am a bit dissappointed. Is this farm coolable and what would be the economical perspective for this application. What solution do you reccommend to me
I will be glad to hear from you. Thanks
 
evolpain:

Sorry if I led you on, but other than giving those numbers, I am by no means a poultry HVAC expert. Like I mentioned, I got those numbers out of a book left over from when I graduatd a couple of years ago.

However, I do work in the HVAC industry ( for a chiller manufacturer). While in college, I worked in the poultry business. I actually lived at the new (new in 1997) poultry facility on campus at Cal Poly.

To be honest, 25,000 birds is not very big. In CA, a fully automated egg production facility ususaly has 1 to 3 million birds. At a central California Foster Farms facility (broilers,) I think they house 15,000 to 25,000 birds in one building, and have over a dozen of them.

Evaporative Cooling is a the only way I have seen cooling for pouldtry done. The cellulose panels are in one side of the building and large fans 24"-36" daimeter pull air across the barn.

I was at a plant today, with a 50 Ton cooling tower. It was roughly 10' in diamter, 8' tall, with a 1 HP fan. 2,000,000 BTU/HR is 166 tons, so in terms or large evaporative cooling, it is not that off the wall.