We need a total of 885 amps of cable ampacity to feed a new AC motor that is replacing a large DC motor.
The new motor is to be fed from a VFD with special 3/C, 350kcmil, 1000V, shielded cable.
The easiest way to do it would be to pull out the old cables and run the new in the existing conduits. One in 3/C in each conduit.
The existing raceway is under the floor in a makeshift duct bank that has 3 PVC pipes and is filled in between the pipes with sand.
The closest detail is Detail 2 as shown in the attached. As you can tell using the 60 RHO column gives an ampacity of 340 x 3 = 1020A, but a 90 RHO 267 x 3 = 801A, not enough. How do you better determine the correct value of RHO ?
The new motor is to be fed from a VFD with special 3/C, 350kcmil, 1000V, shielded cable.
The easiest way to do it would be to pull out the old cables and run the new in the existing conduits. One in 3/C in each conduit.
The existing raceway is under the floor in a makeshift duct bank that has 3 PVC pipes and is filled in between the pipes with sand.
The closest detail is Detail 2 as shown in the attached. As you can tell using the 60 RHO column gives an ampacity of 340 x 3 = 1020A, but a 90 RHO 267 x 3 = 801A, not enough. How do you better determine the correct value of RHO ?