I have generally followed the belief that the oil temp trip (OTT) and winding temp trip (WTT) trip only the LV breaker of the transformer. Should the LV breaker not open within a certain time, then a trip is sent to the HV breaker.
Reasoning has always been that OTT and WTT are not inidcative of trfr unit faults (for that there is Buchholz, diff, pressure relief valve, REF, etc.) but rather overloading (OL). The remedy is thus to shed the load if the trfr is overheating.
This also cures the hotspots as these are related to the current flowing in the windings. With current gone, it is safe to have HV breaker closed and leave trfr energised.
Interested to hear other views/practices.
Thanks.