I have known of several instances that caused a lot of damage, expense and down time. Similar to some of the tales above. Remember that the ac generator (alternator) IEC (and ANSI) specs only require the machine to be designed to sustain a three phase fault on the machine terminals - torques resulting from faulty synchronising are MUCH higher than this. This causes the damage as listed above to keyways, couplings, gearboxes, windings and people. Advice: get it right, make sure procedures and relay sequences do not allow you to get it wrong AND put "check synchronising" relays (separate from the main synchroniser) in the generator breaker "close" circuit - especially if the breaker is remote from the control panel - like it is on most high voltage sets. This will guard against people carrying out a panel wiring modification and shorting out the "close" contacts on the main synchroniser. This can close the breaker as soon as the start button is pressed! A check synch. relay will guard against this - if it is set up right!