- May 17, 2024
- 1
I've just noticed that the heat output of my people gain does not equate to my input at all.
I have set the sensible and latent heat per person to 245 and 205 Btuh respectively.
However on my table the values do not add up.
Should I not have 9,310 Btuh sensible heat gain (38*245)? And 7790 Btuh (38*205) of latent heat gain?
What am I missing here?