SprinklerDesigner2
Mechanical
- Nov 30, 2006
- 1,251
I got a hostpital and have been asked to calculate an additional area consisting of patient rooms and corridor.
Was thinking of going with the largest room method but the partition walls between the patient rooms do not extend to the underside of the deck. With just a suspended ceiling I don't think I can use the smallest room method.
Since I am using quick response and ceilings are <10' I can calculate an area of 900 sq. ft..
Each patient room has a bathroom with lavatory and toilet.
14.4.4.4.2 The requirements of 14.4.4.4.1 to include every sprinkler in the design area to be included in the system discharge shall not apply and where the area of application is equal to or greater than the minimum allowable area of for the appropriate hazard classification (including a 30 percent increase for dry pipe systems), sprinkler discharge in closets, washrooms, and similar small compartments requiring only one sprinkler shall be permitted to be omitted from hydraulic calculations within the area of application. Sprinklers in these small compartments shall, however, be capable of discharging minimum densities in accordance with Figure 11.2.3.1.5.
These are toilet rooms 44.6 sq. ft. each having one sprinkler.
I don't think I have to include the sprinklers in the toilet rooms. There's a total of two toilet rooms.
Are these "Wash rooms"?
Was thinking of going with the largest room method but the partition walls between the patient rooms do not extend to the underside of the deck. With just a suspended ceiling I don't think I can use the smallest room method.
Since I am using quick response and ceilings are <10' I can calculate an area of 900 sq. ft..
Each patient room has a bathroom with lavatory and toilet.
14.4.4.4.2 The requirements of 14.4.4.4.1 to include every sprinkler in the design area to be included in the system discharge shall not apply and where the area of application is equal to or greater than the minimum allowable area of for the appropriate hazard classification (including a 30 percent increase for dry pipe systems), sprinkler discharge in closets, washrooms, and similar small compartments requiring only one sprinkler shall be permitted to be omitted from hydraulic calculations within the area of application. Sprinklers in these small compartments shall, however, be capable of discharging minimum densities in accordance with Figure 11.2.3.1.5.
These are toilet rooms 44.6 sq. ft. each having one sprinkler.
I don't think I have to include the sprinklers in the toilet rooms. There's a total of two toilet rooms.
Are these "Wash rooms"?