DTS419
Structural
- Jun 21, 2006
- 180
Most of us are familiar with the concept of designing a concrete beam for Vu @ d, that is for the shear at a distance 'd' from the face of the support. At this critical distance, the shear in a simple span beam is typically less than at the end or face of support (FOS) which results in a reduction.
Designing for this reduced shear is permitted by ACI 318-19 9.4.3.2 so long as a few conditions are met, one of them being that the beam isn't loaded "such that the shear at sections between the support and a distance 'd' from the support differs radically from the shear at distance 'd'. This commonly occurs in brackets and in beams where a concentrated load is located close to a support...". ACI does not identify how much of a difference is considered a radical difference.
Now let us consider a simply supported single span concrete beam, like a window header, that is supporting floor joists that are spaced at 16" or 24" on center. If the beam is designed using the tributary area approach, it would commonly be designed for a uniform load that would be equivalent to the series of end reactions from the floor joists. But if the beam is designed for the joist end reactions as point loads, then the possibility exists that a joist, or point load, could exist between the FOS and 'd' such that the concrete beam would need to be designed for shear at FOS rather than shear at 'd'.
So would you consider the concrete beam to be uniformly loaded by a series of joist reactions and take shear at 'd', or would you consider the series of joist reactions to be point loads?
Designing for this reduced shear is permitted by ACI 318-19 9.4.3.2 so long as a few conditions are met, one of them being that the beam isn't loaded "such that the shear at sections between the support and a distance 'd' from the support differs radically from the shear at distance 'd'. This commonly occurs in brackets and in beams where a concentrated load is located close to a support...". ACI does not identify how much of a difference is considered a radical difference.
Now let us consider a simply supported single span concrete beam, like a window header, that is supporting floor joists that are spaced at 16" or 24" on center. If the beam is designed using the tributary area approach, it would commonly be designed for a uniform load that would be equivalent to the series of end reactions from the floor joists. But if the beam is designed for the joist end reactions as point loads, then the possibility exists that a joist, or point load, could exist between the FOS and 'd' such that the concrete beam would need to be designed for shear at FOS rather than shear at 'd'.
So would you consider the concrete beam to be uniformly loaded by a series of joist reactions and take shear at 'd', or would you consider the series of joist reactions to be point loads?