when is 4 pole ATS required

Status
Not open for further replies.

skyline1977

Electrical
Aug 6, 2020
3
Hi,
Per NEMA or IEC when are 4 poles ATS required?

 
Replies continue below

Recommended for you

The choice is mostly dependent on the neutral grounding method.
A four pole ATS is used when the neutral must be switched to accommodate grounding requirements.
Many methods of measuring ground fault currents require the use of a four pole ATS.
The code requirement is indirect in that if the ground fault protection requires a switched neutral, then you must use an four pole ATS.


Bill
--------------------
"Why not the best?"
Jimmy Carter
 
In contract with a solid neutral system where a 3-pole ATS is normally used, a 4 poles ATS for is used on a separately derived power system that ultimate is associated with the earthing (grounding) for the emergency system and the ground-fault protection scheme.

Below is a schematic & a switch rendering indicating the neutral pole switched by the ATS.

[sup]>>>>>> [sub]REFERENCES: NEC Sections 230.95,250.24(A)(5), 700.6 (D), K MacKenzie & J. Stark[/sub]<<<<<<[/sup]
03dd02_42afd6c47cf44144bc735a43ca2f3eb1~mv2.jpg


>>>>>
image-15.jpg
 