I'm a degreed EE, but my background is electronics and I could use some help.
BACKGROUND: I'm working at a wind farm site w/ a 34.5 KV collection system. The individual circuits feed into a 34.5 - 345 KV substation. The circuits are typically between 25,000 and 50,000 feet in length, and each has 12-13 2-MW turbines. Cable sizes vary from 3/0 at end of a string to 1250 kcmil on the long runs to the substation and all cable is laid in a trefoil configuration.
ISSUE: Our drawings have the following note on the 1250 kcmil runs to the substation which are ~10,000 feet in length: "Bond cable screens together and to ground at quarter, midway, & three-quarter points along the length of the cable." (This means "cross-bonding", right?) Our developer is saying this is an old note that applied to the orignal plans which did not have the cable in trefoil, but rather, in a flat configuration. They claim the trefoil layout eliminates the need for any cross-bonding.
QUESTIONS:
(1) Am I being fed a line, or is it true that laying cable in trefoil can eliminate the need to do cross-bonding?
(2) What exactly is the purpose of this cross-bonding in this application? I'm guessing it has to do w/ minimizing losses and possibly protection in the event of arcing/lightning, but I'd sure like an educated answer here.
On a related note,
(3) Another issue is the bare ground wire. The drawings call for this to be at the bottom of a 4' trench w/ 6" of grated fill between it and the MV cables. In practice, this is sometimes difficult to achieve. I've seen cases where the ground has been pulled up for some reason and is virtually against the 3 MV cables. Is this something to be concerned about?
Thanks for any help you can offer!
KRCinTX
BACKGROUND: I'm working at a wind farm site w/ a 34.5 KV collection system. The individual circuits feed into a 34.5 - 345 KV substation. The circuits are typically between 25,000 and 50,000 feet in length, and each has 12-13 2-MW turbines. Cable sizes vary from 3/0 at end of a string to 1250 kcmil on the long runs to the substation and all cable is laid in a trefoil configuration.
ISSUE: Our drawings have the following note on the 1250 kcmil runs to the substation which are ~10,000 feet in length: "Bond cable screens together and to ground at quarter, midway, & three-quarter points along the length of the cable." (This means "cross-bonding", right?) Our developer is saying this is an old note that applied to the orignal plans which did not have the cable in trefoil, but rather, in a flat configuration. They claim the trefoil layout eliminates the need for any cross-bonding.
QUESTIONS:
(1) Am I being fed a line, or is it true that laying cable in trefoil can eliminate the need to do cross-bonding?
(2) What exactly is the purpose of this cross-bonding in this application? I'm guessing it has to do w/ minimizing losses and possibly protection in the event of arcing/lightning, but I'd sure like an educated answer here.
On a related note,
(3) Another issue is the bare ground wire. The drawings call for this to be at the bottom of a 4' trench w/ 6" of grated fill between it and the MV cables. In practice, this is sometimes difficult to achieve. I've seen cases where the ground has been pulled up for some reason and is virtually against the 3 MV cables. Is this something to be concerned about?
Thanks for any help you can offer!