That 1.9 MW of load will have the turbos spooled up.On others, starting the largest motor (600 HP pump) on a 3 MVA machine with 1.9 MW of running load works, but starting the big motor in the first load block kills the generator.
Yes.OP said:That's the bottom line question ... can this excessive voltage drop increase the acceleration time of all the motors ?
waross said:600 HP will have a starting kW of about 1.35 kW
When you drop the voltage 10%, the current draw by the motors actually DECREASES. Think in terms of having a Reduced Voltage Autotransformer Starter, just with a 90% tap instead of 50, 65 or 80%. When the voltage is reduced, the starting torque is reduced by the SQUARE of the voltage change. So at 90% voltage, your starting torque is reduced to 81% of normal and since current follows torque, your current is reduced to 81% of the normal starting current. So to answer your question, yes it ABSOLUTELY results in a longer acceleration time, or may in fact result in a stall condition, depending on the acceleration torque requirements of the load.bdn2004 said:That's the bottom line question ... can this excessive voltage drop increase the acceleration time of all the motors ?
This is the real world. You can point to this when someone starts to argue with your numbers.OP said:I’m describing a real incident in this post - where two circuit breakers tripped on startup when they tried to start 3 200 HP motors at the same time: