Eng-Tips is the largest engineering community on the Internet

Intelligent Work Forums for Engineering Professionals

When using metric units, what constant do you use instead of 1.08?

Status
Not open for further replies.

erowe1111

Mechanical
Oct 23, 2007
3
0
0
US
I'm updating some calcs to metric units and for the equation Q=1.08*cfm*delta T, and I don't have access to any air density and specific heat values in metric units. Can someone help me out?
 
Replies continue below

Recommended for you

Q(W) = 1.23 x V(L/s) x dT (K) at sea level.

[link]Air Properties[/url]

Density of air is reciprocal of specific volume, which you can easily get from a psychro chart.

 
a real anal point is that specific volume tells you the volume of moist air, that holds a unit mass of dry air, plus a small mass of water vapour.

Take the "V" out of HVAC and you are left with a HAC(k) job.
 
another question referring to using degrees celsius....

When using bin data in degrees C, is there a standard way to evenly space out the temps? (e.g w/bin data for deg F, there are usually 2.5-5 deg between each temperature)
 
Status
Not open for further replies.
Back
Top