Continue to Site

Eng-Tips is the largest engineering community on the Internet

Intelligent Work Forums for Engineering Professionals

  • Congratulations MintJulep on being selected by the Eng-Tips community for having the most helpful posts in the forums last week. Way to Go!

Where is the prefered location of thermal relief valve on S&T HEX

Status
Not open for further replies.

DoraeS

Petroleum
Mar 8, 2004
44
Dear all, I have a question regarding the thermal relief valve (TRV) location for heat exchanger (HEX).
If I have a cooler with cooling water inlet at HEX bottom and cooling water outlet at HEX top, should I locate my TRV at cooling water inlet (i.e. HEX bottom) or outlet (i.e. HEX top)? Is there any requirements that this TRV should be located on higher location of my cooling water line (i.e. on HEX top, hence CW outlet)? And why is that so?
Thanks for all helps.
 
Replies continue below

Recommended for you

Dora....

Since the function of the thermal relief valve is to protect components under the unlikely case of "valved in" cooling water, placing the relief valve anywhere should be acceptable.

IMHO

-MJC

 
Upstream or down, both are acceptable as MJ points out. Some like to argue one is better than the other, my only requirement is "valve-free" to the HEX. I "prefer" it close.

Something I find more often than not, is use of non-Code RV's (without the UV in the cloverleaf).

 
Both are acceptable, but make sure all the valves on pipe are CSO.
 
Status
Not open for further replies.

Part and Inventory Search

Sponsor