1. Kiribanda
"High Impedance:Since it is having greater stability (during CT sat)for out of zone faults than low impedance version. Mainly used in Bus protection and Transformer (resistance grounded) REF protection schemes. Low cost, simple design, easy testing, needs accurate CT and wiring data to set the voltage setting."
True ( in additional very sensetive and very fast), but...
1.1. Always need special type of CT, for example class X, all CT's must be with same ratio.
1.2 Need exactly calculation of Vx, current wiring loop, resitor and varistor.
2."Low impedance:Low stability for out of zone faults. Mainly used in Bus Protection, Transformer, Generator and Motor Differential protection schemes.Also with present day microprocessor based relays, Transformer REF schemes can have low impedance version too".
2.1 Newer relay could work with few types of CT's ( I say about 87B), with differnce of ratio up to 20:1.
2.2 No problems with stability:
2.2.1 Saturation current reconstraction
2.2.2 Minimum two creterious for operation.
2.3. For the trafo or generator REF, save CT cores and wiring, on the same current inputs you acn build:
2.3.1. Standard diff 87T/87G protection, 87N (REF) protection, 51G, 51N ( BEF, SEF).
Very sensetive setting for REF too ( minimum 1% of Inom)
no neede special trafo on the star point.
2.4 for the 87B BBP protection in the double BB no need
reconnection of current wiring with external relays,
2.4.1 possible build additional logik for the
End fault protection ( dead zone between CB and CT)
BFP are include
Dinamic disconnectors/breakers replica w/o additional relays, that means
Build in check zone functionality. Eazy commissioning, setting, maintanance.
BTW, TODAY, we finished our first project: upgrade of old HI-Z of 170kV power plant SS to the newer LI-Z BBP+BFP, it's tested on-load and back to services.
Best Regards.
Slava