I am checking an exist. 6" slab on grade (f'c=3000 psi)that was designed in the late 1960's. It was supposed to be designed for 10k fork lift wheel loads, however when I use the ACI-360 code and the PCA wheel load charts I am coming up w/ a 7-8 inch required slab. I have also tried the WRI and COE charts. The forklifts have been used for the past 35 years and have not been a major problem. I need to justify a 15k wheel load is okay.
Any suggestions on why my check of the exist. slab won't work for the original design loads?? Are there other methods to use other than the charts mentioned?