Why Delta-Delta Transformers used in Full Static Exciter System 1

Status
Not open for further replies.

CuriousElectron

Electrical
Jun 24, 2017
182
0
0
US
Hello Gents,
I notice that in Full Static Excitation schemes, a delta-delta connected PPT is utilized. Why delta-delta type? My thoughts are that to provide higher reliability - if one phase fails, you can still supply AC power to your power bridge converter via open delta connected PPT. Also, a closed delta connection eliminates third harmonic voltages.
Thoughts?
Thanks,
EE
 
Replies continue below

Recommended for you

On top of advantages you mentioned, low voltage, high current invariably uses delta.

The phase magnetizing currents in 3 phase transformer should contain third harmonics to produce a sinusoidal flux. (The third harmonic present in the phase magnetizing current do not appear in the line current since they are co-phase and hence cancel out in the line.)

A sinusoidal transformer output produces less ripple content in the DC output of the static excitation system which in turn produces a good sinusoidal output from the generator.

Muthu
 
Some codes want the wye point of a wye secondary to be grounded.
A delta winding may be floated, (no ground connection).
In some instances a grounded supply is not allowed for an exciter supply.

--------------------
Ohm's law
Not just a good idea;
It's the LAW!
 