seattlemike
Structural
- Oct 23, 2004
- 79
Hello fellow Structural Engineers,
This may be a dumb point, but 6x6 - W1.4xW1.4 WWM comes up woely short of the ACI requirement of 0.0018.... in a 4" slab, WWM = 0.28 sq in/ft, but ACI requires 0.0018*4*12 = 0.0864 sq in/ft.
what's that all about?
Why does standard Welded Wire Mesh that we always put in slabs not meet ACI shrinkage & temperature criteria (7.12) for slabs with welded wire mesh? Do the joints make up for it instead?
I guess 7.12 is for structural slabs only, and slab-on-grade is not meant to be included.
Mike
This may be a dumb point, but 6x6 - W1.4xW1.4 WWM comes up woely short of the ACI requirement of 0.0018.... in a 4" slab, WWM = 0.28 sq in/ft, but ACI requires 0.0018*4*12 = 0.0864 sq in/ft.
what's that all about?
Why does standard Welded Wire Mesh that we always put in slabs not meet ACI shrinkage & temperature criteria (7.12) for slabs with welded wire mesh? Do the joints make up for it instead?
I guess 7.12 is for structural slabs only, and slab-on-grade is not meant to be included.
Mike