Power0020
Electrical
- Jun 11, 2014
- 303
I feel a bit confused about the requirement. Some standards ask for 0.5 to 1 ohm for EHV substations which is justified by the need for lower GPR and also fast acting protection.
However, for MV installations in IEC world, most of zone substations have an earthing resistance sometimes in the range of 5 ohms, the fault current is limited by NERs usually so that the resultant GPR will not be excessive.
What if the MV neutral point is connected directly to ground? I couldn't figure out any standard recommendation to reduce the resistance. or should it be needed?
However, for MV installations in IEC world, most of zone substations have an earthing resistance sometimes in the range of 5 ohms, the fault current is limited by NERs usually so that the resultant GPR will not be excessive.
What if the MV neutral point is connected directly to ground? I couldn't figure out any standard recommendation to reduce the resistance. or should it be needed?