I'm not an electrical motor expert, but I hope someone can help me. I have a situation where I have an injection molding machine that has a 230v, 3 phase, star-delta start motor. I have gone through 4 motor contactors in 6 months. Some of the time my 100 amp ckt breaker on the wall will trip during the transition from star to delta. Once the machine is running it will remain running with no problems.
When I measure between the legs I have 230v phase to phase and 230v, 230v, and 0v, when measured phase to ground. I was told this was the famous "wild leg" situation. However, reading through the forums here, it sounds like if it was a "wild leg" I should read 120v, 230v, 120v, respectively. I'm confused.
The machine manufacturer tells me that the fact that this is a 3-wire configuration with a wild leg insted of the 4-wire system, this is my problem. The Electric company says it is OK. I have 2 machines doing this and I have replaced all contactors, had motors tested, wiring triple checked, circuit breaker on wall replaced, etc.
I tend to believe the machine technician that the real problem is with the incoming power but I dont know how to prove it or argue the fact.
From reading the forums here I see there are some very talented and knowledgeable people and I'm hoping one of you can help. Thanks.
When I measure between the legs I have 230v phase to phase and 230v, 230v, and 0v, when measured phase to ground. I was told this was the famous "wild leg" situation. However, reading through the forums here, it sounds like if it was a "wild leg" I should read 120v, 230v, 120v, respectively. I'm confused.
The machine manufacturer tells me that the fact that this is a 3-wire configuration with a wild leg insted of the 4-wire system, this is my problem. The Electric company says it is OK. I have 2 machines doing this and I have replaced all contactors, had motors tested, wiring triple checked, circuit breaker on wall replaced, etc.
I tend to believe the machine technician that the real problem is with the incoming power but I dont know how to prove it or argue the fact.
From reading the forums here I see there are some very talented and knowledgeable people and I'm hoping one of you can help. Thanks.