Continue to Site

Eng-Tips is the largest engineering community on the Internet

Intelligent Work Forums for Engineering Professionals

  • Congratulations MintJulep on being selected by the Eng-Tips community for having the most helpful posts in the forums last week. Way to Go!

Will you help my question on fan sizing?

Status
Not open for further replies.

ballsonwalls

Mechanical
Apr 23, 2006
12
I'm new to the industry and I'm a bit confused on sizing supply and return fans.

It seems that supply fans are sized for the external static pressure losses at the outlet. However, a return fan is sized for the static pressure losses at the inlet. Why is this theoretically the case? How does this differ if you have a draw through as opposed to blow through system?

THANK YOU.
 
Replies continue below

Recommended for you

Draw-through or blow-through coils each have their proponents....I prefer draw-through for better flow distribution due to less kinetic effects from high local velocities.
 
The worst case duty for the supply fan is to draw in 100% OA (during economizer cycle) through the OA intake and discharge the air to the most remote/most friction loss supply duct run.

The worst case return fan duty is to pull in return through the most remote/most friction loss return duct run and discharge the air 100% to the relief air discharge during economizer cycle.
 
Status
Not open for further replies.

Part and Inventory Search

Sponsor