VA-Struct-Engr
Structural
- Aug 28, 2019
- 24
Hello everyone.
I am designing a 10-story cold-formed steel (CFS) bearing wall residential building in Mid-Atlantic region. Cladding mostly consists of metal panel and brick. The lateral system is CFS flat strap braced frames. I am looking at building wind drift, designing for 10-year MRI (per ASCE 7-10 Commentary to Appendix C). I am limiting the overall building drift to H/500. Typically, I would limit the story drift to maximum of H/500 or 3/8”, however, my floor-to-floor height is only 9’-8” in this building (floor structure is shallow). H/500 for this height is 0.23”, which seems conservative to me, so I am thinking of reducing this requirement to H/360 (0.32”). Does anyone have any thoughts on this? Does it seem reasonable to reduce the floor-to-floor drift requirement or should I stick with H/500?
Thank you for your inputs in advance.
I am designing a 10-story cold-formed steel (CFS) bearing wall residential building in Mid-Atlantic region. Cladding mostly consists of metal panel and brick. The lateral system is CFS flat strap braced frames. I am looking at building wind drift, designing for 10-year MRI (per ASCE 7-10 Commentary to Appendix C). I am limiting the overall building drift to H/500. Typically, I would limit the story drift to maximum of H/500 or 3/8”, however, my floor-to-floor height is only 9’-8” in this building (floor structure is shallow). H/500 for this height is 0.23”, which seems conservative to me, so I am thinking of reducing this requirement to H/360 (0.32”). Does anyone have any thoughts on this? Does it seem reasonable to reduce the floor-to-floor drift requirement or should I stick with H/500?