Wind speed for fire fighting Model

Status
Not open for further replies.

zishan99

Mechanical
Mar 11, 2006
15
Which wind speed (average or maximum)will considered for model an oil terminal fire fighting system.What is the limit of wind speed to be considered.
 
Replies continue below

Recommended for you

I would be inclined to use the maximum wind speed which has been recorded historically for fifty (50) years at the location of the plant. For a measure of comfort, I would then use an additional ten (10) percent.

This would represent the worst case scenario in your model and drive the design to handle for maximum loads.

Just my two (2) cents worth.

Kenneth J Hueston, PEng
Principal
Sturni-Hueston Engineering Inc
Edmonton, Alberta Canada
 
I'd have thought your insurance company would have an opinion on the matter.

Cheers

Greg Locock

Please see FAQ731-376 for tips on how to make the best use of Eng-Tips.
 
Worst case has to be rotor wash from news helicopters.



Mike Halloran
Pembroke Pines, FL, USA
 