Hey Guys,
I'm having a little trouble with a couple of things and was hoping you guys could clear up my mis-understandings with the whole Wye and Delta arrangements. I'm going to use a standard 277/480 system as the basis for discussion.
In a Wye arrangement the Phase to ground voltage is 277V. While the phase to phase is 480V. To me that makes perfect sense because phase to ground you are looking at a positive voltage to a non-potential ground and getting some voltage. When you look phase to phase you are seeing a positive voltage to a negative voltage in the other phase, thus you are seeing the 480V. Mathematically you can derive why the phase to phase voltage peaks before the phase to ground and whey the phase to phase voltage is Sqrt of 3 times more. Intuitively you can see this by looking at a three phase wave form as well.
In a delta arrangement, I don't understand this quite so well.
What do you see if you look at the phase to ground voltage of a delta system? I assume you would see 480V, because teh absolute magnitude of the voltage in teh system with reference to gound would be 480V.
Also if this is true I understand why a Delta to Wye transformer needs more winding on the Wye side. This is because in the winding the effective voltage on the delta side is 480 volts and you are only gettign 277 on the wye side.
Given this, would a delta generator have a different number of windings rather than a wye generator? Intuitively I would say no, because the connection to teh other phases would provide the absolute voltage (between the positive in one winding and the negative in the other)
If anythign I am asking is unclear or incorrect please let me know and I will try to explain further. I am a mechanical engineer trying to learn electricity. Please take pity on me.
Thanks,
Rob
I'm having a little trouble with a couple of things and was hoping you guys could clear up my mis-understandings with the whole Wye and Delta arrangements. I'm going to use a standard 277/480 system as the basis for discussion.
In a Wye arrangement the Phase to ground voltage is 277V. While the phase to phase is 480V. To me that makes perfect sense because phase to ground you are looking at a positive voltage to a non-potential ground and getting some voltage. When you look phase to phase you are seeing a positive voltage to a negative voltage in the other phase, thus you are seeing the 480V. Mathematically you can derive why the phase to phase voltage peaks before the phase to ground and whey the phase to phase voltage is Sqrt of 3 times more. Intuitively you can see this by looking at a three phase wave form as well.
In a delta arrangement, I don't understand this quite so well.
What do you see if you look at the phase to ground voltage of a delta system? I assume you would see 480V, because teh absolute magnitude of the voltage in teh system with reference to gound would be 480V.
Also if this is true I understand why a Delta to Wye transformer needs more winding on the Wye side. This is because in the winding the effective voltage on the delta side is 480 volts and you are only gettign 277 on the wye side.
Given this, would a delta generator have a different number of windings rather than a wye generator? Intuitively I would say no, because the connection to teh other phases would provide the absolute voltage (between the positive in one winding and the negative in the other)
If anythign I am asking is unclear or incorrect please let me know and I will try to explain further. I am a mechanical engineer trying to learn electricity. Please take pity on me.
Thanks,
Rob