Performing a short circuit study at a commercial facility. Many of the local disconnects at 5 and 20 horsepower motors are for disconnect purposes only. I have typically indicated that a non-fused disconnect would have a withstand rating of 5,000A. My short circuit calculations indicate 15,000 for many of the disconnects.
Is my assumption that 30 and 60A heavy duty safety switches have a relatively low withstand, like 5k?
I can't find withstand information on the manufacturers site for a disconnect without the use of fuses (which fuses are not installed anywhere in the circuit, just breakers, MCP's and overloads).
Is my assumption that 30 and 60A heavy duty safety switches have a relatively low withstand, like 5k?
I can't find withstand information on the manufacturers site for a disconnect without the use of fuses (which fuses are not installed anywhere in the circuit, just breakers, MCP's and overloads).