Wood Partition at 33kV Substation

Status
Not open for further replies.

eskim

Electrical
May 25, 2003
19
0
0
ID
Dear All,

I just found out that on one of our Substation has wood partition to seperate Switchgears and fiber optic junction boxes.

Is there any regulation about this, because in my opinion this is a fire hazard.

If some one out there could advise me the regulation i would be glad and certainly this wood partition will be remove.

thanks
 
Replies continue below

Recommended for you

Wire communication equipment is often mounted on wood boards to insulate remote ground from station ground. Ground Potential Rise (GPR) is not a problem with fiber optic cables, but maybe it is a holdover from past telephone company standards.
 
Most of our 15kV-isolated pilot wires for feeder differential protection (mainly translay) are in wooden cabinets, to maintain the isolation. Maybe the fibre comms you have just replaced some old copper links which also had a high isolation level?



Bung
Life is non-linear...
 