Hello all,
need help in figuring out reinforcement approach to one of mandatory soft-story projects that i'm handling now.

So it's a 4-story building and I'm trying to reinforce one of sides with wood shearwall.
However, since I can only place shearwall one side, i.e. outside, as placing shearwall inside gets complicated due to presence of tenants, I can't seem to meet the requirement. I believe I should consider using moment frame, but I was wondering if using thicker plywood could increase allowable shear diaphragm values.

SDPWS2015 only provides the values up to where 19/32" plywood is used. So does that mean I won't be able to use thicker plywood by code? If I ever could do so, any idea where I can maybe find those related information?

I flipped through SDPWS, CBC and NDS but couldn't find solid solution to this.

Thanks in advance!
 
Replies continue below

Recommended for you

Plywood shearwall capacity is governed by the nailing. Thicker plywood will not give you ever increasing shear capacities.
"...if using thicker plywood could increase allowable shear diaphragm values."
Make sure you are using the shear wall table from the SDPWS not the diaphragm table. They have different values.

If I had such high unit shears on a 4 story building I'd make sure I can even make the holdowns and foundation work.
 