Wood Waffle Ceiling & Ceiling Pocket Coverage

Status
Not open for further replies.

tys90

Mechanical
Jun 15, 2007
157
We have been tasked with adding sprinkler coverage to a building with a historic wood waffle ceiling. We are not allowed to modify the ceiling per the State Historical Preservation Office. I believe this ceiling qualifies as having ceiling pockets per NFPA 13 8.6.7.1. They meet all the exceptions of NFPA 13 8.6.7.2 except with it being wood, it does not meet item (5) of being noncombustible or limited-combustible.

Am I interpreting this correctly that these pockets need coverage?

The AHJ has hinted they would consider a variance due to the historic nature but we need to detail how the space would be covered underneath, which is another challenge without creating an eyesore.

2022-04-04_12h06_46_r7jgh1.png
 
Replies continue below

Recommended for you

Ouch

How deep are the pockets

Kind of looked like they have been modified in the past. ???
 