Continue to Site

Eng-Tips is the largest engineering community on the Internet

Intelligent Work Forums for Engineering Professionals

  • Congratulations GregLocock on being selected by the Eng-Tips community for having the most helpful posts in the forums last week. Way to Go!

WYE-DELTA AS A GROUNDING TRANSFORMER 1

Status
Not open for further replies.

genhead

Electrical
Jul 26, 2001
71
How is a wye-delta transformer connected as a grounding transformer. I have only used zig-zag previously.
 
Replies continue below

Recommended for you

Wye-Delta transformers are natural grounding transformers, provided that central star point is connected to ground. Wye windings sould be connected to side to be grounded. Zero sequence currents to ground are looped by the opposite delta windings.
Zig-zag transformers need only one winding to play as grounding ones, in such a way that in some cases they are not strictly transformers, but three-phase coils Julian
 
The wye-delta connection for grounding is deceptively simple. The delta winding is left floating (or grounded at one bushing only). The wye side is the “ground source” the same way that a zigzag would be. [Imbalanced] currents at the wye-side neutral point will cause a circulation of current in the delta ‘ring.’ In some cases this ‘feature’ becomes a ‘bug’ of sorts; for instance where a distribution circuit serves has multiple transformer banks with grounded-wye primaries. Both become sources for zero-sequence current but, IIRC the zigzag configuration uses less copper and steel for an otherwise equal rating.
 
Status
Not open for further replies.

Part and Inventory Search

Sponsor