Scenario is as follows:
I have a 460VAC, 60Hz,3 phase, 1750RPM, 500Amp induction motor designed to
operate on a 480VAC Wye start/ Delta run starter system.
When a different motor was tested on this machine, it starts properly and
there is little load on the dual output shafts(About 25% of the full load
amps).
Each shaft has a hydraulic pump attached that spins easily.
The Main breaker trips off when the problematic motor transfers from Start
to Run.
Why?
The motor has 12 leads.
They are numbered as follows: 1,1 2,2 3,3 4,4 5,5 and 6,6.
The motor leads continuity test as follows:
1,1 to 4,4.
2,2 to 5,5.
3,3 to 6,6.
The motor is connected to the starters as follows:
L1 to 1,1 L2 to 2,2 L3 to 3,3 on the Main breaker (no Main contactor)
L1 to 6,6 L2 to 4,4 L3 to 5,5 on the Delta run contactor
6,6 4,4 5,5 on the Wye start contactor also.
The phasing from the Main breaker to the motor leads connections has been
verified as correct for the Wye/Delta configuration.
The Main breaker is a 700Amp shunt trip breaker. It can be shunt tripped from the Overload relay or motor thermal sensors, as well as tripping from overcurrent. The adjustable trips are set at Maximum.
The starting sequence is:
The Wye start contactor is closed first.
The motor ramps up to speed in the correct rotation.
After 5 seconds the Wye start contactor opens and the Delta run contactor
immediately closes.
Wham! The breaker trips.
Why?
I have a 460VAC, 60Hz,3 phase, 1750RPM, 500Amp induction motor designed to
operate on a 480VAC Wye start/ Delta run starter system.
When a different motor was tested on this machine, it starts properly and
there is little load on the dual output shafts(About 25% of the full load
amps).
Each shaft has a hydraulic pump attached that spins easily.
The Main breaker trips off when the problematic motor transfers from Start
to Run.
Why?
The motor has 12 leads.
They are numbered as follows: 1,1 2,2 3,3 4,4 5,5 and 6,6.
The motor leads continuity test as follows:
1,1 to 4,4.
2,2 to 5,5.
3,3 to 6,6.
The motor is connected to the starters as follows:
L1 to 1,1 L2 to 2,2 L3 to 3,3 on the Main breaker (no Main contactor)
L1 to 6,6 L2 to 4,4 L3 to 5,5 on the Delta run contactor
6,6 4,4 5,5 on the Wye start contactor also.
The phasing from the Main breaker to the motor leads connections has been
verified as correct for the Wye/Delta configuration.
The Main breaker is a 700Amp shunt trip breaker. It can be shunt tripped from the Overload relay or motor thermal sensors, as well as tripping from overcurrent. The adjustable trips are set at Maximum.
The starting sequence is:
The Wye start contactor is closed first.
The motor ramps up to speed in the correct rotation.
After 5 seconds the Wye start contactor opens and the Delta run contactor
immediately closes.
Wham! The breaker trips.
Why?