DistCoop
Electrical
- Jan 2, 2013
- 83
All,
I've searched the forums and was surprised to see this hadn't been addressed, so if I've overlooked something, please let me know.
I have a three phase wye-delta 12.47kV to 240V with a tap on one delta leg for 120V. The wye is ungrounded, and the tap on the delta is grounded.
How would one calculate a LN fault between either of the 120V phase-neutral legs? How is the fault calculated for the 208V to neutral phase? Let's say that the neutral is on the AB winding, so Van and Vbn are 120V, Vcn is 208V, and the line-line voltage between any phase is 240V.
Thanks