wroggent
Electrical
- Aug 20, 2012
- 288
Working on a project where the local utility will supply the transformer for a new facility (13.2kV wye/480V wye, 750kVA). Incoming voltage is 12.47kV. We will be using a high resistance ground on the 480V side to limit SLG faults to 10A. Positive and zero sequence impedances of the utility network from the point of connection are negligible compared to what would be typical of a 10A grounding resistor for 480V systems. Are there any issues to be concerned about specifically regarding the high side winging configuration (grounded wye)? I am more familiar with a delta high side for a setup like this. The only thing I can think of is if there was a loss of the neutral connection on the high side then there would be no path for zero sequence current on the low side (with the exception of through the magnetizing reactance of the core, I guess). I'm not sure if that is likely enough to occur to warrant a concern though. What is your experience with this?