DM61850
Electrical
- Sep 9, 2019
- 80
I have an auxillary wye 1:1 120V grounded broken delta transformer that is feeding a Basler 59N relay. When I hooked up a test set to the secondary of bus PT's (15 kV:120V) I was seeing voltage any of the phases when I pulled it from the test set. I thought it was a wiring issue at first but I figured out that the broken delta regenerates the voltage on the high side of the auxiliary PTs/low side of the bus PTs. Is this something that is just inherent if you have this type of a transformer. I don't have a second set of PT's to use to separate the broken delta. I am concerned that my transfer scheme might misoperate during a blown pt fuse or loss of a phase.
I haven't found much on this but I found this NERC lessons learned where a utility had a misoperation due to a wye-broken delta pt backfeeding a phase that had a blown fuse.
How much concern should I have of a wye-broken delta transformer backfeeding voltage to my relaying? My transfer scheme depends solely on line and bus voltages.
I haven't found much on this but I found this NERC lessons learned where a utility had a misoperation due to a wye-broken delta pt backfeeding a phase that had a blown fuse.
How much concern should I have of a wye-broken delta transformer backfeeding voltage to my relaying? My transfer scheme depends solely on line and bus voltages.