Yes, the equation you have is based on the interconnection of the 3 sequence networks for a single line to ground fault and will result in the equivalent X/R ratio for this condition.
If you are using it to compute duty of ANSI rated circuit breakers you actually have to calculate the X using an X only network and the R using an R only network.