steelerfan28655
Electrical
- May 6, 2004
- 40
One of our customers has requested fault current data for the secondary side of their transformer bank. They have a Y-Delta, 240 volt, three phase, four wire service, with two 50 kVA and one 75 kVA, 7200 to 120/240 transformers. The center tap of the 75 kVA provides the load side neutral. My question is, how to calculate the fault current at the secondary spades. I have read different practices including the worst case scenario of treating all three transformers as if they were 75 kVA.
The single phase to ground primary fault current is 4326 amps. Three phase to ground is 5710 amps.
High side: R1=0.3853, X1= 1.2038, R0=0.8923, X0=2.3132
Z= 1.65% for the 50 kVA's and 1.6% for the 75 kVA.
I have done many of these for single phase services and for grounded wye three phase services. However the split secondary of the different size transformers has me wondering how to incorporate the differences in impedances into a common secondary bus.
Any help would be appreciated. My boss has already denied my request for a subscription to the IEEE library.
Happiness is a way of travel, not a destination.
The single phase to ground primary fault current is 4326 amps. Three phase to ground is 5710 amps.
High side: R1=0.3853, X1= 1.2038, R0=0.8923, X0=2.3132
Z= 1.65% for the 50 kVA's and 1.6% for the 75 kVA.
I have done many of these for single phase services and for grounded wye three phase services. However the split secondary of the different size transformers has me wondering how to incorporate the differences in impedances into a common secondary bus.
Any help would be appreciated. My boss has already denied my request for a subscription to the IEEE library.
Happiness is a way of travel, not a destination.