reandy
Industrial
- Jun 27, 2005
- 5
Ok, simple question I hope.
Normal for the U.S. (me anyway) 480 VAC 3ph, 9 lead motor. Internally lead #10, #11, & #12 are connected together, making it a Y motor. If this is normal, and it is in Y for run, why do we Start in Y and run in Delta?
Ok, this is what I am thinking... In Y we have to go thru 2 'winding sets' to get from phase to phase, and in delta we only have to go thru 1 'winding set'. Ok, makes sence, but...
Then we would need a 'special'(higher voltage) motor for Y Start/Delta Run. I mean, you couldn't just use a 12 lead motor and make it Y/Delta. The name plate says for high voltage:
L1-T1
L2-T2
L3-T3
T4-T7
T5-T8
T6-T9
T10-T11-T12
and it mentions nothing for a delta connection. The motor runs fine.
So my question can be distilled to, can I just connect this motor for Y Start / Delta Run? Because it is already in a Y Run?
I am thinking that when I would switch it to Delta, it would be getting too much voltage in each winding. Isn't the Phase to Phase winding count 4 in Y, and only 2 for Delta (assuming High Voltage connection)
So the only conclusion I can come to is that for a Y Start / Delta Run motor, I need a motor that can handle Full Voltage in the Delta Configuration, and it would get partial voltage in the Y Configuration?
Is it this simple? or is there more to this?
Thanks
Reandy
Normal for the U.S. (me anyway) 480 VAC 3ph, 9 lead motor. Internally lead #10, #11, & #12 are connected together, making it a Y motor. If this is normal, and it is in Y for run, why do we Start in Y and run in Delta?
Ok, this is what I am thinking... In Y we have to go thru 2 'winding sets' to get from phase to phase, and in delta we only have to go thru 1 'winding set'. Ok, makes sence, but...
Then we would need a 'special'(higher voltage) motor for Y Start/Delta Run. I mean, you couldn't just use a 12 lead motor and make it Y/Delta. The name plate says for high voltage:
L1-T1
L2-T2
L3-T3
T4-T7
T5-T8
T6-T9
T10-T11-T12
and it mentions nothing for a delta connection. The motor runs fine.
So my question can be distilled to, can I just connect this motor for Y Start / Delta Run? Because it is already in a Y Run?
I am thinking that when I would switch it to Delta, it would be getting too much voltage in each winding. Isn't the Phase to Phase winding count 4 in Y, and only 2 for Delta (assuming High Voltage connection)
So the only conclusion I can come to is that for a Y Start / Delta Run motor, I need a motor that can handle Full Voltage in the Delta Configuration, and it would get partial voltage in the Y Configuration?
Is it this simple? or is there more to this?
Thanks
Reandy