A greenhouse customer has ordered 277V lighting fixtures (46 x 660W for each of 3 houses), needs to run on a generator for short grows, then roll everything up, take to other sites on a rotating annual basis (so everything is temporary/portable). My task is to provide wiring, etc.
One of my schemes uses 5 conductor 600V SO cable, 4 strings per house, 1st half of each string 8/5, second half 12/5, each on a 3 pole 30a breaker (with whatever contactors/timers end up being needed, with 16/3 pigtails to individual fixtures from fiberglass J-boxes, everything overhead). Reading around here, I'm thinking I may need to up-size for the neutrals depending on harmonics of the fixtures (which the supplier does not specify), but also I've seen suggestions that 1 pole breakers are required somehow. I would think the 3 poles would be safer? Also something about a ground fault wiping out whole banks of ballasts?
I would appreciate any feedback - don't much like the idea of a bunch of 480V cords running around but don't see another way . . .
One of my schemes uses 5 conductor 600V SO cable, 4 strings per house, 1st half of each string 8/5, second half 12/5, each on a 3 pole 30a breaker (with whatever contactors/timers end up being needed, with 16/3 pigtails to individual fixtures from fiberglass J-boxes, everything overhead). Reading around here, I'm thinking I may need to up-size for the neutrals depending on harmonics of the fixtures (which the supplier does not specify), but also I've seen suggestions that 1 pole breakers are required somehow. I would think the 3 poles would be safer? Also something about a ground fault wiping out whole banks of ballasts?
I would appreciate any feedback - don't much like the idea of a bunch of 480V cords running around but don't see another way . . .