I am checking an existing building for the addition of new equipment that will be suspended from open web joists. The drawings list a variety of 22H and 24H joists in the different locations. The added equipment will increase the moment in the steel joists beyond the published acceptable value and the customer wishes to suspend between the panel points of the joists in order to align with floor mounted equipment for the assembly line. We can add a new internal chord at the hanger location, but still need to check the joists, so we are analyzing them as trusses.
The issue I have is that the publication I am looking from Vulcraft lists a base yield strength of 50 ksi for the chords of H-series joists. The building was put up in the 70's and the chords are only 2x2 double angles. I find it hard to believe that they have a yield strength of 50 ksi, yet I can't find any publication to support me, or I overlooked it. My preference would be to assume A36 for all of the members. Does anyone have an alternate course of action?
The issue I have is that the publication I am looking from Vulcraft lists a base yield strength of 50 ksi for the chords of H-series joists. The building was put up in the 70's and the chords are only 2x2 double angles. I find it hard to believe that they have a yield strength of 50 ksi, yet I can't find any publication to support me, or I overlooked it. My preference would be to assume A36 for all of the members. Does anyone have an alternate course of action?